    I have a standard 50 amp 220V socket that I have used just for my miller mig welder. My garage is the typical garage that was built in the 50's that came with just two 15 amp 110V plugs. I would love to have a converter that i can then wire some extra 110V sockets. What would you recommend?
     
  2. jimjimjimmy

    jimjimjimmy lobsterman FABO Gold Member

    Messages:
    4,601
    Likes Received:
    1440
    Joined:
    Nov 2, 2010
    Location:
    p. e. i.
    Local Time:
    5:48 AM
    I think you could just come off one side of the 220 . 220 is just two 110's on the hot side .
    a converter changes AC to DC . A Inverter changes DC to AC .
     
    • Agree Agree x 1
    • Jesus Chrysler

      Jesus Chrysler Forgiving Sins Against Mopar Since 1983

      Messages:
      270
      Likes Received:
      216
      Joined:
      Feb 5, 2018
      Location:
      Ontario, California
      Local Time:
      1:48 AM
      Nay verily, I proclaim. If the "220" power in the garage is your typical single phase 240v welder circuit there will be no neutral conductor and thus, no code compliant/safe return path for a 120v load.

      If you want to break some 120v power off the existing 240v receptacle you would need a small transformer to derive a neutral, which would be cost prohibitive to purchase and install properly. A 240v single phase 50a receptacle will be a NEMA 6-50R and will only have 3 prongs. If this is what you have then chances are there is no neutral conductor. A 50 amp 120/240v single phase receptacle with neutral would be a NEMA 14-50R and will have 4 prongs. Considering most welders use single phase power in either 200/230/460 volts, I'd be really surprised if there was a neutral available at that plug.

      Just pay a sparky to run a couple extra 120v circuits to the gayrage. It's your best bet...
       
      Last edited: May 22, 2018
      • Agree Agree x 2
      • jimjimjimmy

        jimjimjimmy lobsterman FABO Gold Member

        Messages:
        4,601
        Likes Received:
        1440
        Joined:
        Nov 2, 2010
        Location:
        p. e. i.
        Local Time:
        5:48 AM

        Thanks that AC current is sketchy stuff
         
      • Jadaharabi

        Jadaharabi FABO Gold Member FABO Gold Member

        Messages:
        8,698
        Likes Received:
        9783
        Joined:
        Jan 8, 2016
        Location:
        Peoria, Illinois
        Local Time:
        3:48 AM
        Hire a good electrician.
         
        Last edited: May 22, 2018
      • Dfr360cuda

        Dfr360cuda Diagnosis... Plum Crazy.

        Messages:
        1,767
        Likes Received:
        1137
        Joined:
        Aug 30, 2012
        Location:
        Finleyville, PA
        Local Time:
        4:48 AM
        Run a new feed.
        Install a sub panel
        SAFETY FIRST.
         
        • Agree Agree x 1
        • Dana67Dart

          Dana67Dart Like a fine wine, only getting better with age! FABO Gold Member

          Messages:
          6,568
          Likes Received:
          4331
          Joined:
          Jul 16, 2017
          Location:
          Northern Colorado
          Local Time:
          2:48 AM
          what do you plan on running on the extra 120V outlets?
           
        • 67Dart273

          67Dart273 FABO Gold Member FABO Gold Member

          Messages:
          48,759
          Likes Received:
          16869
          Joined:
          Oct 14, 2010
          Location:
          Idaho
          Local Time:
          1:48 AM
          OK, let's straighten this out!!!

          IF YOU HAVE (like me) an older setup ---I use "dryer plugs" WHICH ARE NOT a neutral!!!! They are TWO wire plus ground, which is the green/ safety ground AND NOT NEUTRAL!!1

          Therefore you CAN NOT (legally) use this for 120V (I do anyway LOL)

          50-amp-plug.jpg

          HOWEVER.........every 240V welder I've seen in the last 40 years had a FOUR WIRE PLUG!! This means it has TWO hot conductors plus the NEUTRAL plus the green/ safety GROUND

          Each HOT is 120V to NEUTRAL. This means you have TWO 120V circuits in that plug

          N%2014-50R%20125-250-volt.jpg

          So IF you have a 4 terminal/ slot/ conductor receptacle, you could wire it for 120 EXCEPT FOR THE following:

          You have a HUGE (30-40-50? amp) breaker feeding that circuit, and that is NO PROTECTION AT ALL for 120V outlets.

          IF YOU ONLY want something temporary, I would get a small 2- breaker box and put som 15 or 20A breakers in there, and then wire it with a plug to fit the welder receptacle...........go to the box........and then either more cord to something like a couple of receptacles in a box, or mount the box right on the back or bottom of the breaker box.

          WHAT YOU HAVE

          GROUND/ green is for SAFETY, it hooks directly to the breaker box and the receptacle box, as well as to the green screw on the receptacles

          You will need to devise some way of "stepping down" the big wire from the welder plug to fit the breakers. Wire nuts, or careful selection of breakers and your "welder cord" they might fit fine as is

          One hot to each breaker, green to the box, and white / neutral gets connected to the white screws on the receptacles, so this will have to be clamped with a terminal/ wire nuts etc and passed on to the receptacles.
           
          Last edited: May 22, 2018
        • 67Dart273

          67Dart273 FABO Gold Member FABO Gold Member

          Messages:
          48,759
          Likes Received:
          16869
          Joined:
          Oct 14, 2010
          Location:
          Idaho
          Local Time:
          1:48 AM
          So "how" do I get away with using a 3 terminal plug (no neutral) for occasional 120V and WHY would I do that?

          FIRST, at my junkhouse, the 240V welder box comes DIRECTLY off the main breaker box. AT THE MAIN BOX the is where main power comes in, and the neutral buss, and the ground buss and the box ground ALL AMOUNT TO THE SAME TERMINAL. This is NOT the case with added breaker boxes / sub panel such as "over at the house." (My main is at the detached garage)

          At the house breaker box, which in this case is actually a sub-panel, the box is grounded to a stake, and is grounded to a ground / green conductor coming from the garage. The NEUTRAL at the house box is connected to an INSULATED neutral buss bar, NOT THE CASE at the garage main panel

          If you open my box, there is about 2ft total wire "or less" between the box for the welder, the main box, the neutral, and the ground buss. They are one and the SAME

          So I have "cheated" and tied the neutral and ground together on my 120V adapter. They are one and the same.

          I ONLY do this when I want to use the 120V MIG "far from" the house, as I have a couple of long "welder" extension cables

          This is NEVER plugged in for more than long enough to get the job done, certainly not unattended or overnight.

          So far as grounding, it is safe because everything that is a "box" is grounded including the welder, which ALSO has a 3 wire plug
           
        • Jadaharabi

          Jadaharabi FABO Gold Member FABO Gold Member

          Messages:
          8,698
          Likes Received:
          9783
          Joined:
          Jan 8, 2016
          Location:
          Peoria, Illinois
          Local Time:
          3:48 AM
          Get an electrician to look at what you have.
           
          Last edited: May 22, 2018
        • 67Dart273

          67Dart273 FABO Gold Member FABO Gold Member

          Messages:
          48,759
          Likes Received:
          16869
          Joined:
          Oct 14, 2010
          Location:
          Idaho
          Local Time:
          1:48 AM
          To be clear this is not a "system." This is a temporary lashup to get 110 (120) at fairly high current "once in awhile.

          All US household electrical systems have more than one ground. You sound like you are in Europe? Whole different deal. Here, the 240V neutral is grounded at the pole and at the main box at the house, AKA "meterhead"
           
        • Jadaharabi

          Jadaharabi FABO Gold Member FABO Gold Member

          Messages:
          8,698
          Likes Received:
          9783
          Joined:
          Jan 8, 2016
          Location:
          Peoria, Illinois
          Local Time:
          3:48 AM
          Good luck.
           
          Last edited: May 22, 2018
        • Jadaharabi

          Jadaharabi FABO Gold Member FABO Gold Member

          Messages:
          8,698
          Likes Received:
          9783
          Joined:
          Jan 8, 2016
          Location:
          Peoria, Illinois
          Local Time:
          3:48 AM
          It's not worth dying over. Hire an electrician.
           
          Last edited: May 22, 2018
        • Jadaharabi

          Jadaharabi FABO Gold Member FABO Gold Member

          Messages:
          8,698
          Likes Received:
          9783
          Joined:
          Jan 8, 2016
          Location:
          Peoria, Illinois
          Local Time:
          3:48 AM
          Hire an electrician.
           
          Last edited: May 22, 2018
        • 67Dart273

          67Dart273 FABO Gold Member FABO Gold Member

          Messages:
          48,759
          Likes Received:
          16869
          Joined:
          Oct 14, 2010
          Location:
          Idaho
          Local Time:
          1:48 AM
          I don't need anybody to look at anything, and you are incorrect, please re-read this thread

          1....The OP was looking for a way, I only wrote how I do it. The only thing that is not "code" is the TEMPORARY grounding on the rarely used extension cord

          2....There ARE more than one ground on a house system. The house main box ground is the "start" that is the line neutral and the box case ground and the ground stake are all tied together there

          When you wire up a sub panel in another building THAT is grounded at that box so IT has a separate ground. That's at least TWO right there

          3....If you have a tower IT is grounded by means of multiple ground stakes, and if it has power to it THAT is tied to the tower and therefore tied to the main system ground. That's THREE

          4...Plumbing......Gas pipe and plumbing is often bonded to the house system ground and "yes" the gas meter and house water supply both have "dielectric" connectors, but this doesn't mean that an outside faucet might be tied to something else. "Possibly FOUR"

          5...Lightning protection.....Some houses have various types of lighting (rod) protection, and THAT is grounded by means of multiple stakes as well as bonded/ tied to the house main ground

          SO THAT'S at least FIVE...........separate.......grounds depending on the situation.

          Another? ANY metal equipment, such as a welder, or in my case, the outdoor two post hoist. The electrical ground is tied to the metallic box and conduit on the hoist. So the entire hoist is connected to system (green) ground.......traced directly back to the main box.

          THE HOIST sits on the GROUND on a metal frame. Isn't that "ground?" I'd think so.
           
        • Jadaharabi

          Jadaharabi FABO Gold Member FABO Gold Member

          Messages:
          8,698
          Likes Received:
          9783
          Joined:
          Jan 8, 2016
          Location:
          Peoria, Illinois
          Local Time:
          3:48 AM
          Good luck
           
          Last edited: May 22, 2018
        • Jesus Chrysler

          Jesus Chrysler Forgiving Sins Against Mopar Since 1983

          Messages:
          270
          Likes Received:
          216
          Joined:
          Feb 5, 2018
          Location:
          Ontario, California
          Local Time:
          1:48 AM
          I see where you are coming from, but a couple things should be clarified:

          The "ground," or equipment grounding conductor, AKA green wire, AKA bare copper wire, is meant to provide a low impedance path back to the transformer in order to clear faults on electrically conductive materials that people may come in contact with. The way it does this is via the neutral tap of the supply transformer, where it will be bonded ONLY at the main panel, as you have pointed out.

          Grounding electrodes, AKA ground rods, cold water pipe, etc. are meant only to help keep metal items at ground potential and to dissipate residual fault current into the earth. They are not meant to be the low impedance path needed to open a circuit breaker and eliminate hazardous voltage from metal items that we come in contact with.

          The ground at your "sub panel" is tied only to the chassis of the panel at this point because connecting it to the neutral bus would turn every ground wire and bonded piece of equipment/junction box/conduit downstream into a neutral conductor. We call this "objectionable current", and it is dangerous.
           
          Last edited: May 22, 2018
          • Thanks! Thanks! x 1
          • Agree Agree x 1
          • DavidLee

            DavidLee Well-Known Member

            Messages:
            329
            Likes Received:
            71
            Joined:
            Aug 1, 2011
            Location:
            Torrance, CA
            Local Time:
            1:48 AM
            i am going to have my panel replaced in a short period of time. I will just ask them to add a few more plugs into the garage. That will give me an excuse to clear the garage and paint the floor at that time.
             
            • Like Like x 2
            • Louie70Dart

              Louie70Dart Back home in K-Town WI. Woo Hoo

              Messages:
              3,923
              Likes Received:
              2720
              Joined:
              May 3, 2010
              Location:
              WI
              Local Time:
              3:48 AM
              Hmmm, I have a 220 in my basement for dryer that I don't need cause the one I have is gas. I was wondering about breaking the 220 down and run to garage for more juice. Now it's 110 at 15 amps. Sounds as though it is a little more involved than just splitting it in half. I am not versed in electric at all, so this is not for me. Thanks to OP for this thread! And thanks to 67Dart273 also for the info.
               