Electricians on FABO - I want to add a 60Amp sub panel
It does not have the spot at the top to install a 60Amp main breaker. I was told I didn't need one - if I want to shut off power when in the garage, I could shut off all the breakers. Any thoughts?
Put the 60a breaker in your main panel in your house. Run the #6 to the lugs in your sub panel. Seperate the grounds and neutrals in the sub panel. If you want to shut off power in the garage, simply turn off the circuit breakers in the garage.
I run 12/3 Romex, you might use the black for outlets and the red for lights. This way if you trip a breaker from plugging something in, the lights will still work. And using 12/3 cuts the neutrals and grounds in half, sort of neating up the panel.
Looks good, you know what the heck yer doing. I did the same thing in my garage. Had my fusebox replaced in the house along with the fusebox there was a 60A breaker style ponypanel....told the elec I wanted the pony panel in the shop. It has a "main" shutoff and the house now has breakers. I rented a trencher and buried the wire in conduit approx 18" deep. No extra ground rods were needed. Inspector chkd and passed it all.
Oh I knew people that with the old style meters where the "wheel" spun around..in order to get around their hydro bills, they would take a rubber mallet and a light "swat" to the meter..would knock the wheel "off" so it couldnt track the hydro usage..
Codes say 18" is OK with conduit, don't bury it 4 feet deep. Strap the vertical conduit to the building at midpoint. Keep the neutral separate from the ground, including the box. Do pound a ground rod next to the new panel location and tie it to the ground bus in the new panel using solid #6. Your wire is rated for damp only locations, if the conduit fills with water you might have a problem, THWN would be better in that case. Panel without main breaker is not best, but meets code. I like a main so I can shut off the panel in sight, sucks if you are working on it and someone turns the breaker on when you can't see it. Your wire (#6) is rated for 65 amps and should be just fine, you could use a 70 amp CB to feed it if you wanted. Be careful and wear good dry leather gloves if working around hot power, electricity is not very forgiving. You should consider GFI on your circuits, 2011 code requires it, though which code applies depends on where you live. I am a licensed electrical engineer and design these for a living, so need to tell you it is probably legal to do your own wiring but you should get a permit! (Don't want any lawyers calling me) Be careful and good luck!
Thanks guys! I did install a 60amp main breaker on the subpanel and pounded an 8' ground rod for the subpanel. The hardest part of the job was digging the freakin trench 18" deep with a pick and a trench shovel - 30 feet long.
IIRC, schedule 80 PVC is code for your vertical runs. It wouldn't pass here without it. Also, at least two ground rods at least 8' apart are mandatory at the outbuilding side.
Good move on running a ground seperate from the neutral.
Older post, looks like the OP figured it out but posting this anyways as it may help others down the road. I am planning this next weekend. Heres an article I found earlier on gardenweb and a picture from diy.
What should I know about installing a subpanel?
No electrical wiring FAQ would be complete without addressing the issue of subpanels. If, after reading the article below, you have any questions or feel that your situation is not covered by the article, please visit the Electrical Wiring Forum to ask any follow-up questions.
A very special thanks to Tom_O for writing this article and sharing it with us.
This is a general guideline about the installation of a sub-panel in a remote building, hopefully it will contain the information you need. At the bottom will be a list of items you can omit if the sub-panel will be located in the same building as your service entrance. Most of the requirements would apply to any structure, but I have aimed this at installations on residential property.
If your installation is subject to inspection, you should talk to your local code enforcement official prior to starting work.
Wire - Type and size
You can use underground cable. The following capacities apply for copper cables:
Cable ampacities - 60C temperature rating
#10 - 30 amps
#8 - 40 amps
#6 - 55 amps (can be protected at 60 amps)
#4 - 70 amps
#2 - 95 amps (can be protected at 100 amps)
If you elect to use cable, it will need to be protected from damage if it emerges from the ground on the exterior side of a building. This protection can be rigid metal conduit, intermediate metal conduit or schedule 80 PVC. The protection must extend from the bottom of the trench to the height of 8' above grade, or where the cable enters the building, whichever is less.
The preferred method is to run PVC conduit with individual conductors. The minimum size should be 1 1/4", as this will allow you to run up to a 100 amp feeder. The following capacities are for copper conductors with THWN, THW or XHHW insulation:
Individual conductor ampacities - 75C temperature rating
#10 - 30 amps
#8 - 50 amps
#6 - 65 amps (can be protected at 70 amps)
#4 - 85 amps (can be protected at 90 amps for outbuildings. If this sub-panel is in a dwelling #4 may be good for 100 amps - see notes below)
#3 - 100 amps
Please see the notes at the end regarding wire ampacities and temperatures!
Number of conductors needed
For various reasons, it is best to run 4 conductors. This would be two 'hots', one grounded conductor (neutral) and one equipment ground (bare or green).
Depth of trench
For cable, you will need 24" of cover. For PVC conduit, you will need 18" of cover.
While you have your trench open, you should put in at least one spare conduit (3/4" minimum size) for future use. It would be a shame to dig up your yard again just to run a phone line.
Sub-panel main breaker
At your remote building, your sub-panel must have a main breaker if there will be more than six breakers used in your panel. It is recommended to put in a main breaker even if only a couple of circuits will be used initially. If the main breaker is to be back-fed, it must be held in place by a screw or clip that will prevent it from being unplugged by hand. You can use a 100 amp breaker even if the size of the feeder circuit is less, however, check the wire range allowed for the connection to the breaker to make sure that the wire size you are using is within the acceptable range for that particular breaker.
Grounding and bonding of the sub-panel
At the sub-panel there must be no connection between the neutral bus bar and the equipment ground bus bar or the neutral bus bar and the sheet metal of the breaker box. You may need to purchase an additional bus bar for the equipment ground since many panels, especially those that come with a main breaker, do not come equipped with one. If the panel comes with a bonding screw or bonding strap, do not install it to the neutral. Depending on the brand of panel, you may need it to connect the ground bus to the sheet metal enclosure.
At the remote building, you will need to drive two eight-foot ground rods located a minimum of six feet from each other and connect them to the equipment ground bus using #6 copper wire. The easiest way is to make one continuous run without cutting the wire. The rods must be driven in flush or below grade. The ground rod clamps must be listed for direct burial. It will say so on the clamp or look for the letters "DB". If you have any metal piping (except gas lines) in the remote building, you must bond it to the equipment ground bar, use #6 wire. If the connection is to a metal water line, the connection should be within the first 5 feet of where the water line enters the building. All connections must remain accessible, so if the connection will end up inside a wall, you must provide an access plate.
I realize that some of the things I've included exceed the code minimum, but this is an attempt to make a "one size fits all" response without getting into a really long discussion.
For a sub-panel in the same dwelling there is no need for additional ground rods or connections to metal piping. Also, no need for a main breaker in the sub-panel, regardless of the number of circuits. Unless you are running metal conduit, you will need to run a 4 wire feeder.
Wire ampacity notes
If you are installing a sub-panel in your house, the ampacity of #4 copper or #2 aluminum is 100 amps as determined by a special table in the code. However, in some jurisdicitons, there is a very strict interpretation of this table and these ampacities would not be allowed for a sub-panel in your house. If you aren't sure, ask your inspector if he will allow the ampacities shown in table 310-15(B)(6) or go up one size wire to #3 copper or #1 aluminum.
The current carrying capacity of an insulated conductor is related to the type of insulation. Modern insulation allows conductors to be operated at higher current levels which generate more heat. There is a problem if you install the modern conductors into an older service panel as the higher temperatures could damage the older types of insulation. If your home was wired prior to 1985, you may have conductors with a lower rated insulation. If you have an older home or aren't sure, to be on the safe side, use the wire capacity table above that deals with cables. The larger conductors that you will use will now be in the same temperature class as the older styles of insulation.
Circuit breaker notes
Circuit breakers and panelboards also have a temperature rating. Most modern circuit breakers will be marked 60/75 C. This means that this circuit breaker can be used with wire being operated at its 75 degree C rating without doing damage to the circuit breaker.
However (there always seems to be one of those), the entire panel must be listed for use at that temperature. Older panels will not have the higher temperature rating. In order to find out if your existing panel is rated for 75 degree ampacities, you will need to read all of those fine print labels. For us older guys, that means break out the magnifying glass. You cannot just stick a new circuit breaker into an old panel and assume that it will be safe.
During your exploration of all the fine print, you should be looking for some indication that 75 degree wire can be used at its full temperature rating. What you're hoping to see is a reference to 60/75C for conductor sizes #14 to #1 AWG. If you don't see the 75 degree listing, then the wire must be operated at the 60 degree rating, therefore use the table above for cables to select the correct wire size.
Article written by Tom_O
UPDATE:
I got an estimate from an electrician that came in at $1500....and he would use aluminum #2 wire.
The distance between the garage and house is 27 Ft. and although I've had two back surgeries in my past for a herniated disc, there is no way I am paying that just because of my reluctance to dig.
From talking to the electrician, I know it has to be buried 18" for code.
The panel I want to buy from Home Depot is a GE 125Amp. It does not have the spot at the top to install a 60Amp main breaker. I was told I didn't need one - if I want to shut off power when in the garage, I could shut off all the breakers. Any thoughts?
I am lisc. in ct.
60a cb at house panel.
The sub panel needs to have a means of disconnect. if it has a main cb in it thats fine.you can only use the branch circuit cbs as a means of disconnect if there are no more than six.
18" burial in conduit. 1" pvc
(3) #6 cu L1 L2 and nuetral
(1) #8 cu grnd
(2) ground rods at detached garage. jump together w/#6 and run that #6 to sub panel and bond to panel box via a ground bar made for the panel. Your ground wire from the house will also conn ect to this ground bar.
The nuetral bar that comes with the sub-panel should not be electricaly bonded to the sub panel box it should "float".
If there is any metal piping water or gas it needs to grounded to the panel box. Especialy if it runs between the buildings.
At the house panel if it has the 200 amp main in it, then the ground and nuetral can go on either the ground or nuetral bar, makes no difference.
If the main is not in it then keep the ground and nuetral on thier respective bars. It will be obviouse. If you need more help you can pm me and we can talk. Tomorrow. You can do this but needs to be correct. I assume you will sell this house some day and wouldnt want anyone getting hurt so you could save 1500? Another idea would be to see if your building dept would issue a home owners permit. Then you could get it inspected and they would point out whats wrong.